The fall is an excellent time for maintenance to prevent losses from occurring during the winter months. First up should be making sure that all exposed pipes and piping on exterior walls are maintained as to prevent them from freezing.
Additionally the following is some basic guidance on proactive facility maintenance:
Preventive Maintenance Checklist
ROOFING
Save yourself from recurring issues and unexpected failures by using a roof asset management program. This strategy syncs preventive maintenance and inspections with corrective action, ultimately extending the time between roof replacements.
✓ Inspect at least twice a year and after any severe storm.
✓ Create a roofing file for each building; review warranty information.
✓ Clear roof drains of debris (roof warranties don't cover this).
✓ Walk the perimeter to examine sheet metal, copings, and previously repaired sections.
✓ Check roof-to-wall connections and examine flashings (at curbs and penetrations, etc.) for wrinkles and tearing.
✓ For single-ply roofs, re-caulk the top of face-mounted termination bars (if needed).
✓ For bituminous roofs, check for splits in the stripping plies.
✓ Be on guard against corrosion on metal roofs, which may be caused by condensate from copper coils in rooftop HVAC units. Duct the condensating water to keep it from coming into contact with the membrane.
✓ Keep traffic off of the roof to avoid membrane damage.
✓ Don’t let your green roof die from lack of care. Be attentive to plant health by monitoring growth and weeding and trimming as needed. Proper irrigation is not only critical for the survival of vegetation but also protects your roof membrane against leaks and ponding.
✓ Plan a moisture survey every 5 years to detect wet insulation or leaks.
✓ If you have a rooftop solar array, be aware that panels can become dislodged by a buildup of ice and snow. Inspect the racks and areas around penetrations during your regular walkthroughs. You can also mount ballasted systems on a pad to protect the roof membrane from possible damage.
HVAC
Spend some quality time with your heating and cooling equipment to preserve energy efficiency and indoor air quality.
✓ Inspect at least twice a year, with seasonal start-up and run inspections. Look for screw or latch updates, gasket repairs, and missing screws replacements. Also recharge P-traps or U-bend water traps for condensate drain pans.
✓ Seasonal PM of chillers and boilers is involved; industry practice is to have a qualified mechanical contractor provide services.
✓ For cooling towers, disassemble screens and access panels for inspection; inspect the tower fill, support structure, sump and spray nozzles, fill valve, gear box, drive coupling, fan blades, and motor bearings; clean starter and cabinet; inspect wiring; check motor starter contacts for wear and proper operation; megger test the motor and log readings; and check the condition of the sump heater and contactor, and log observations.
✓ Pumps usually require bearing lubrication at least annually. Inspect couplings and check for leaks. Investigate unusual noises.
✓ Air handling unit maintenance should include cleaning or replacing air filters at least once a month, though some may only need to be changed every 3-6 months.
✓ If you can reach the condenser coil, simply buy coil cleaner, apply and wipe off. If you need to remove panels to access the coil, use a licensed contractor.
✓ Periodically inspect settings for energy efficiency, particularly the compressor, refrigerant charge and thermal expansion valve (if applicable).
✓ In direct pressure systems, confirm that the superheat temperature falls between 10-20 degrees F. Look up the evaporating temperature per the manufacturer that corresponds with the measured suction line pressure, then measure the actual suction line temperature – the difference between these two numbers is the superheat temperature.
✓ Have an economizer? Dampers can malfunction if they become corroded or jammed with debris. Keep tabs on all moving parts, including the actuator and linkages, as well as seals. Properly calibrate sensors at least once a year.
James Hale, ARM-P, ARM-E
Risk Control Consultant
County Risk Sharing Authority
209 East State Street
Columbus, OH 43215
614.246.1630 FAX 614.220.0209
“ The leader in providing Ohio Counties with exceptional value, service, and protection of assets.”
CONFIDENTIALITY NOTICE: This e-mail message (including any attachments) is intended only for the person or entity to which it is addressed and may contain confidential and/or privileged material. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy this message and all attachments.